2 x 24V banks in parallel


  • Hello,

    I am looking to setup a LFP power system for a boat with 16 EVE LF280K cells configured in 8S2P for a total of 560Ah @24V and looking to use REC 2Q BMS for each 8 cell string.

    Can I just use 2 separated REC 2Q BMS for each string, each BMS with its own shunt and relays, and program them indipendently, obviously with same settings (LVD, HVD, etc.) ?

    I have a mix of Victron (solar MPPT) and non-victron (inverter/charger) components 

    Do I have to purchase a REC BMS MASTER UNIT as well ? Is it mandatory?

    A master-slave config looks quite complex. 

     

     

     

     

     



  • for a 560Ah system, as long as you have well behaved cells, you can likely use a single 2Q BMS by connecting them in a 2P8S configuration.

    If you want a redundant system you will need 2 of the 2Q BMS's with a Master which makes them look like one complete pack to the Victron, as it will accept one DC source (but can monitor more)

    Here is a link to a sing 2Q BMS in a 2p8S config diagram:

    https://rec-bms-na.com/download/45/rec-2q-bms-sketches/1323/rec-2q-series-bms-with-victron-and-ws500-diagram-rec-q-24v-2p-8s.pdf

     


  • and here are a few pics of what a Master/Slave system displays on a Victron Cerbo