I am preparing to install a LFP battery on a sailboat and am trying to pin down a BMS. REC seems to be the best. I have multiple charging sources that are fairly "dumb" with no CAN controls or even "disable" controls (Balmar regulator, wind generator, towed generator). My solar is all Victron and so is my inverter/charger (MP2), but I do not have (nor want -- a lot of money for not much use for me) any GX devices.
I intend to have one main contactor (the Blue Seas 7713). All charge sources will be direct to the main bus, and tripped by control wires (inverter, solar, and 270A of alternators) or in-line contactors (probably Victron Battery Protect).
My sequence of voltages (specific numbers to be determined) are:
* HVC (open main contactor)
* HVA (alarm and disable charging sources)
* Charge source setpoint
* Working region
* Inverter internal cutoff
* LVA and disable inverter
* LVC (open main contactor)
My questions:
1) Can the HVC and LVC be controlled by a single relay, or do I have to run the control through both BMS relays? Seems a waste to consume both onboard relays to control one contactor? Are they "dry contacts" so I can run through them in series?
2) By ABYC, a pre-alarm is required for any disconnect. There are 4 outputs (2 relays and 2 optos), and my design uses all 4. Unfortunately, the HVA would also be the "charge enable" opto coupler, resulting in many alarms (or I configure all charge sources below the HVA and lose the ability for the BMS to control charge sources -- not necessarily bad) Ideally, I could recover the HVC relay, and use it for a HVA.
3) Is it best to run the BMS on the load side, or the battery side, of the main disconnect? Since there is very little chance of the main disconnect ever opening in the life of the battery, it's probably academic, but how does the BMS handle a loss of power (does it loose, for instance, SOC?).
4) I will be using the WiFi adapter. The LCD does not appear to be available (is that correct? Every time I try and build an order, I can't find it anywhere). I will be retaining my ancient but excellent LINK 2000, which will still give me Volts, Amps, and its version of SOC (probably 99% of what I'll ever want to know). Am I OK using the Link for day-to-day monitoring, and the WiFi when I want details?
5) The manual talks about a "Discharge Algorithm" that slowly dials back discharge. Given that all loads are a set value, how is this accomplished? An inverter is on or off (the microwave draws a fixed amount!). Same with DC loads -- I can't control the amount of power the chart plotter draws. Is this unique to some specific use-case (say, grid-tie systems)? Can this be disabled, or is this just ignored and has no impact on systems that don't have controllable/variable loads?
Thanks for any input!