There can be many poles, but its still 3 phases. There is really no "middle" phase. They will all give an pulse you can use for pulse to rpm. You can add an diode in series to it.
There can be many poles, but its still 3 phases. There is really no "middle" phase. They will all give an pulse you can use for pulse to rpm. You can add an diode in series to it.
I dont kow the DC Power Engineerng alternators specific. But, if you open the lid on the back of the alternator you wil see 3 thick wires coming out from the alternator going in to the recti...
Hi. You were all correct, there WAS an bad connection on the solid red wire. It was impossible to see from the outside and even when pulling it, feeld snug. But I cut of the connector and crimpe...
Below is an log from when turning on ignition gives error #43. Seems like an internal HW error to me. Sep-24-2023,08:56:38,0, ,AST;,0.02, ,13.07,6.9,6.9,90, ,14.30,490,150...
Hello. My WS500 has started giving Error 43, Alternator Low voltage. But the alternator voltage is just fine. AST;,0.00, ,13.06,-32.6,-32.6,-425, ,14.30,490,15000,10, ,25,33, ,0, ,13.06,26,-99,2...
@Michael We have the 4JH4 54 HK motor with dual 200A alternators. Having one on each side of the motor helps with the side-load issues. Been working great for many years now but we do not use the...
I have the same setup in my boat. 60% field max at normal drive (about 230A). Then 90% when "I need to charge quick mode" (about 400A). Could probably change it to 40%/90%.
@Michael There is an "feature inn" cable on the WS500 for this, its all in the manual. "The Feature-in port allows a wide range of optional capabilities in the WS500 to be selected in real time. T...
If you activate DVCC then REC BMS becomes "the boss". But its allways good to set some reasonable (low) settings in the Multiplus as fallback.
I did get an reply from Tine about this. And from my understanding all BMS`s send ID 0x3.. And this can be changed to 0x4.. with special FW for BMS but then you need to customice programmin...
Hi. I currently have two REC A-BMS connected to the same Cerbo. One BMS is ID 2 and other is ID 4 in RS485 network, so far so good. But when I connect them both to CAN-BUS there seems to be some...