Victron BMV Settings


  • Hi All

    I have a 1120Ah LifePO4 battery, a REC BMS, a Cerbo GX, a Multiplus II and a WS500.

    I am getting significant different SOC readings between the REC BMS and the Victron BMV. I think the charged voltage on the BMV is too high(14.2v) and so the monitor is not re-synchronising when the BMS. I also wonder what settings on the BMV that are not quite correct.

    I wondered if there was a "Cheat Sheet" or if anyone had a list of the settings that I should be using???



  • Yes, it is indeed to high. Try setting the Charged Voltage to 13.9V.