Have a Master BMS were the external fuse was blowed. Now the BMS will not start up.
Is there any fuse inside the unit?
Power supply is 48 V in to BMS.
Hi,
Have a Master BMS were the external fuse was blowed. Now the BMS will not start up.
Is there any fuse inside the unit?
Power supply is 48 V in to BMS.
I can't ever rember a Master failing so we have never had one apart. Grab a Torx#10 and slide off the cover. If its like the BMS's look for a small black/brown approximately 1cm square with a dab of silicone. It just pulls out of the socket.
If no luck, REC has a repair/return process. Just contact Maja at maja@rec-bms.com
If you need a replacement right away and want to keep the other as a spare, it looks like we have a couple in stock currently.
https://ogm-energy.com/products/rec-master?variant=44098283700543
Let us know what you find :)