who is the boss? BMS or Multiplus?


  • Hello,

    A very simple question : I use the REC Active BMS with v2.90 firmware connected to Cerbo and multiplus.
    There are max voltage settings for absorption and float.
    Do they still have any effect or is it the REC BMS that commands the Multiplus charging?

    Thx

    Carl



  • If you activate DVCC then REC BMS becomes "the boss".

    But its allways good to set some reasonable (low) settings in the Multiplus as fallback.

     


  • @carl The cerbo should show, external control, in the multi dialog.  In victron connect app, MPPT's, shows also external control.  WS500 shows, state 39, in logfile.

    The MAX voltage setting under DVCC, overruled the BMS input, set this always a bit higher as the BMS max voltage.


  • Thanks that makes this clear