I used a 2.94 from another sourse as from
https://rec-bms-na.com/product-manuals/#7-8-wpfd-rec-active-bms
Now I downloaded the version from the link above.
Installed it, it worked perfect.
Restart an extra time, all worked, still connection with Cerbo.
Strange why it didnt work on yours.
Double check or GX, Services/VE.CAN port/CAn bus profile is set at (Ve.can & VE-bus BMS(250kbits/s)
After changing CANS 2, speed 250, you did a restart?
Extra note:
Nothing todo with NO communication, but after upgrade to 2.94, the new function MODE is at 1.
See info from txt file at download link.
MODE 1 is for Main relay, charge and discharge switch off
MODE 2 is for main relay, only discharge switch off. FOR charge switch off, program relay 1 under TASK.
One more note:
See new function, which I personally like and Iam happy it is finally there.
UBDI (End of charge allowed cell voltage difference)
I set this to 0.025 instead of the factory setting from 0.008