I have the BMS connected to Cerbo GX, which is also connected to a Multiplus 3000. I have enabled DVCC/SVS/STS like the BMS manual suggests and I am running an unexpected problem: when I disconnect the BMS from the Cerbo, or when I disconnect the Multiplus from the Cerbo, the Multiplus continues charging.
I would\'ve expected that if there is loss of communication the Multiplus will abort charging. Going over an Orion BMS manual, which is also Victron-CAN compatible, they do indicate that loss of communication should prevent the Multiplus from turning on.
The Cerbo GX manual also indicates that in the section where they describe what happens if you power up the CerboGX from the Multiplus AC ouput, but in my setup for whatever reason if I power up the Multiplus with the Cerbo turned off, it is still happy to charge - which is unacceptable for safety reasons...
Does anyone have any idea what I am missing?
I\'m attaching some photos of the information displayed on the Cerbo.
Thank you!