I just installed twin engine wakespeed regulators with Balmar alternators. Both Alternators are connected to the house batteries. Wakespeed current sense wires are connected to de...
I just installed twin engine wakespeed regulators with Balmar alternators. Both Alternators are connected to the house batteries. Wakespeed current sense wires are connected to de...
Just installed a couple of WS500s on a catamaran. Using the latest FW 2.5.1 with ENABLE_ALT-CAN set to option 18 to use the Victron shunt as the battery shunt. Have alternator shunts installed as w...
@D. Ryan I was actually able to reconfigure how the network recognized the data without downgrading it, after changing some settings. But this is without Cerbo, I plugged it straight into the B&...
@Rick I'd love to see an update to this post!
DId this downgrade fix your issue? Are you still seeing canbus data on your Cerbo?
Still waiting for updates to this from Victron or Wakespeed on the new option in V2.5.1 to take data direct from a Victron SmartShunt through the Cerbo GX. Will it only work with a SmartShunt or an...
I can not think of any way to do this in the settings. The only way would be a normally closed relay to invert the output but that results in current draw which may not be possible depending on you...
Here is a WS500 pinout diagram that I grabbed from this forum and annotatwed it with a cross-reference to the numbering used in the user install manual. Let me know if you find any typos.
I pulled the WS500 pinout dirgram from another post on the site and have added in the cross-reference to the harness wire numbers used in the install manual. If you find any typos, let me know and ...
It looks like Victron has changed links again. Victron Cerbo GX <--> Wakespeed WS500
I would pay $$ for such a guide. Especially if there was someone that was keeping it up to date. I know that this forum is a great source of info, but the "forum" format makes it hard to pull out j...
Hey, I want to have the feature in wire activate half power mode when voltage is applied to the feature in wire. The only option I can see in the app is "select half power mode (inverted ...
Same here. Good luck brother 😅
From your description it sounds like this will work just fine for you by interupting the remote on/off switch. And yes, the switch will power down your BMS, with all parameters saved.
I have a split bus and use the REC BMS to control contactor on load bus and charge bus. I want to have an emergency shut down switch that will safely shut down the entire lithium system.&nbs...
I have read all of the available and sometimes conflicting documentation re how to set up, and configure the WS500 <--> Cerbo GX <--> REC-BMS set up. It is like I am panning for ...
I've created a Node-Red flow that solves this problem perfectly. It has a dashboard interface to enable/disable the scheme. It also sends an email when the Victron Multiplus mode is aut...
Raymond, thanks for that information. Chris
@Christopher I have found for the Victron BMV-712 to match the REC Active using (1.04) Peukert exponent works well.
Thanks Rick, just sent it.
Sure, just send a quick email to support@ogm-energy.com and we will send it to you
Hello everyone, I recently upgraded the firmware to 2.5.1 but unfortunately this broke the display of NMEA alternator data (temperatures, rpm, current, etc) on my B&G Zeus3. This was something ...
@Peter Well The resistors inside the BMS are 4Ohms, this means when balancing @ 2.5V that is minimum threshold it would be 0.625 A when balancing, but actually a bit lower since the BMS perf...
Thank you Rick. In order to use the two 2Q slaves, do you also need a Master unit?
We havent ever had to use this but hopefully Tine from REC can help @Tine Andrejasic
Hi Peter, I can answer a few questions here for you. There is an extra output that can be configured using the Tasks section of the WiFi for your ssplit bus system For a 22 cell configuration yo...
Hi, this is my first post, as I just found this company as a reseller of REC BMS. I'm building a new battery system for my double-split-phase Sunny Island backup power system. The battery will co...
I'm trying get my external battery monitor to match with the SOC calculation performed by the BMS. I'd like to know the Peukert exponent used by the BMS. Thanks, Chris
This project is still alive but moving slowly. We hope to be able to put some real time into it this summer
From Bob Pogue One major thing that I see that is missing is a manual charge initiation option. You’ll often want to fill the pack while driving even though it hasn’t reached its disch...
I wonder if there is an issue with the module 2 precharge unit. The 6 pin descriptions are different than the newer 10 pin and possibly (probably) miswired in some way. In particular mi...
If the Cerbo is also powered on the system side then it does not get the data from the BMS when disconnected.
@tine Yes there is a contactor and it is connected in the positive.
Charge current is only set to 0 A when the temperature goes under the Under-temperature for charging. Contactors are ON unless you select them in the TASKS for the charge relay 1.
No can't do. It does not work like this. Victron CAN bus protocol was provided to us and all the CAN data is supported. To get the Time to go, they would have to add this feature or a programmer sh...
@Christopher Is the Quattro connected to the BMS via a contactor. IS the contactor in positive or negative?
I did a test. Installed a fresh downloaded firmware. Made the suggested settings. All worked. (I use a test setup, with 4 LED to monitor all outputs) Advise, double check firmware version. Aft...